Cause : NV Media Card has the Read Only bit set comes when the C.rdo trip indicates that an attempt has been made to modify data on a read-only NV Media Card or to modify a read- only data block. A NV Media Card is read-only if the read-only flag has been set.

  1. Clear the read only flag by setting Pr 00 to 9777 and reset the drive. This will clear the read-only flag for all data blocks in the NV Media Card.