C.rtg fault error 186 in unidrive C200 nidec control techniques drive
Cause : NV Media Card Trip- The voltage and / or current rating of the source and destination drives are different comes when the C.rtg trip indicates that parameter data is being transferred from the NV Media Card to the drive, but the current and / or voltage ratings are different between source and destination drives.
  1. This trip also applies if a compare (using Pr mm.000 set to 8yyy) is performed between the data block on a NV Media Card and the drive.
  2. The C.rtg trip does not stop the data transfer but is a warning that rating specific parameters with the RA attribute may not be transferred to the destination drive.
  3. Reset the drive to clear the trip.
  4. Ensure that the drive rating dependent parameters have transferred correctly.
  5. This trip can be suppressed by setting Pr 00 to 9666 and resetting the drive.
