Cause : NV Media Card parameter set not compatible with current drive mode comes when the C.tyP trip is produced during a compare if the drive mode in the data block on the NV Media Card is different from the current drive mode.
  1. This trip is also produced if an attempt is made to transfer parameters from a NV Media Card to the drive if the operating mode in the data block is outside the allowed range of operating modes, for the target drive.
  2. Ensure the destination drive supports the drive operating mode in the parameter file.
  3. Clear the value in Pr 00 and reset the drive.
  4. Ensure destination drive operating mode is the same as the source parameter file.