Cause : Trip initiated from the Control Word (06.042) comes when the CL.bt trip is initiated by setting bit 12 on the control word in Pr 06.042 when the control word is enabled (Pr 06.043 = On).
- Check the value of Pr 06.042.
- Disable the control word in Control Word Enable (Pr 06.043).
- Bit 12 of the control word set to a one causes the drive to trip on Control Word.
- When the control word is enabled, the trip can only be cleared by setting bit 12 to zero.