EF0 fault code in NE300 nidec control techniques drive

1 Posts
1 Users
0 Reactions
141 Views
Posts: 17564
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Communication fault comes when no control data was received from the connected PLC when using serial communications.

Typically "EF0" fault occurs when a drive is communicating with a PLC via Modbus, BACnet MS/TP, Apogee, or Metasys and communication is lost for the duration of time set in parameter.

  1. Baud rate and parity checksum is set incorrect- check communication parameters correct or not.
  2. Communication interrupted for long time- check the interface wiring.