Forum

Share:
Notifications
Clear all

EF2 fault code in NE300 nidec control techniques drive

1 Posts
1 Users
0 Reactions
170 Views
Posts: 17563
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Terminal close fault comes when the FWD or REV terminals close and get power on. But inverter is set to not allow the restart after power failure recovery.

  1. Disconnect the FWD or REV terminal first and then power on the inverter.
  2. Close the fault detection function for closed terminal fault (FC.11=0).
Share: