EF2 fault code in NE300 nidec control techniques drive

1 Posts
1 Users
0 Reactions
245 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Terminal close fault comes when the FWD or REV terminals close and get power on. But inverter is set to not allow the restart after power failure recovery.

  1. Disconnect the FWD or REV terminal first and then power on the inverter.
  2. Close the fault detection function for closed terminal fault (FC.11=0).