Cause : Data processing error- CRC check on the firmware has failed comes when the HF19 trip indicates that the CRC check on the drive firmware has failed. The drive is now in its bootloader mode and is waiting for a new image to be downloaded using Connect. Once a new image is downloaded, the drive can run normally.
- This is a hardware fault and cannot be reset.
- Check drive hardware.
- Re-program the drive with latest control and power firmware using Connect.