Forum

Share:
Notifications
Clear all

It.Ac fault error 20 in commander C200 nidec control techniques drive

1 Posts
1 Users
0 Reactions
287 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Output current overload timed out (I2 t) comes when the It.Ac trip indicates a motor thermal overload based on the Motor Rated Current (Pr 05.007) and Motor Thermal Time Constant (Pr 04.015). Pr 04.019 displays the motor temperature as a percentage of the maximum value. The drive will trip on It.AC when Pr 04.019 gets to 100 %.

  1. Ensure the load is not jammed / sticking.
  2. Check the load on the motor has not changed.
  3. Tune the motor rated speed parameter (Pr 05.008) (RFC-A mode only).
  4. Ensure the motor rated current is not zero.
Share: