nidec c200 drive fault codes
nidec c200 drive fault codes - if you are facing any fault in nidec drive then below list help you to identify fault and its solution:
Trip Code Condition Possible Cause
C.Acc NV Media Card Write fail Unable to access the NV Media Card
C.by NV Media Card cannot be
accessed as it is being accessed
by an option module
An attempt has been made to access a file on NV Media Card,
but the NV Media Card is already being accessed by an option
module. No data is transferred.
C.cPr NV Media Card file/data is different
to the one in the drive
A C.cPr trip is initiated if the parameters on the NV Media Card
are different to the drive
C.d.E NV Media Card data location
already contains data
Attempt has been made to store data on a NV Media Card in a
data block which already contains data.
C.dAt NV Media Card data not found Attempt has been made to access non-existent file or block on
the NV Media Card.
C.Err NV Media Card data structure
error
Attempt has been made to access the NV Media Card but an
error has been detected in the data structure on the card.
Resetting the trip will cause the drive to erase and create the
correct folder structure.
C.FuL NV Media Card full There is not enough space left on the card.
C.OPt NV Media Card trip; option
modules installed are different
between source drive and
destination drive
The parameter data or default difference data is being
transferred from the NV Media Card to the drive, but the option
module category is different between the source and destination
drives.
C.Pr NV Media Card data blocks are not
compatible with the drive derivative
If Drive Derivative is different between the source and target
drives. Refer to the Control User Guide.
C.rdo NV Media Card has the Read Only
bit set
Attempt has been made to modify a read-only NV Media Card or
a read-only data block.
C.rtg NV Media Card trip; Option module
file transfer has failed
The C.SL trip is initiated, if the transfer of an option module file
to or from a module failed because the option module does not
respond correctly.
C.tyP NV Media Card parameter set not
compatible with current drive mode
The drive mode in the data block on the NV Media Card is
different from the current drive mode.
cL.A1 Analog input 1 current loss Current loss was detected in current mode on Analog input 1
(Terminal 2).
CL.bt Trip initiated from the Control Word Initiated by setting bit 12 on the control word when the control
word is enabled. Refer to the Parameter Reference Guide
Cur.c Current calibration range Current calibration range error.
Cur.O Current feedback offset error Current offset is too large to be trimmed.
d.Ch Drive parameters are being
changed
A user action or a file system write is active that is changing the
drive parameters and the drive has been commanded to enable.
dEr.E Derivative file error Contact the supplier of the drive.
dEr.I Derivative product image error Contact the supplier of the drive.
dESt Two or more parameters are
writing to the same destination
parameter
The dESt trip indicates that destination output parameters of two
or more logic functions within the drive are writing to the same
parameter.
dr.CF Drive configuration Contact the supplier of the drive.
EEF Default parameters have been
loaded
The EEF trip indicates that default parameters have been
loaded. The exact cause/reason of the trip can be identified from
the sub-trip number (Refer to the Control User Guide).
Et An External trip is initiated The cause of the trip can be identified from the sub trip number
displayed after the trip string.
Sub-trip = 1 Reason - External Trip =1
FAn.F Fan fail Indicates the fan or fan circuitry has failed
Fi.Ch File changed A file has been changed, power cycle to clear the trip
FI.In Firmware Incompatibility The user firmware is incompatible with the power firmware
HFxx trip Hardware faults Internal drive hardware fault (Refer to the Control User Guide).
It.Ac Output current overload timed out
(I2t)
The It.Ac trip indicates a motor thermal overload based on the
output current and motor thermal time constant. The drive will
trip on It.Ac when the accumulator gets to 100 %.
This can occur when:
• There is excessive mechanical load
• Ensure the load is not jammed / sticking
• Check the load on the motor has not changed
• Ensure the motor rated current is not zero
It.br Braking resistor overload timed out
(I2t)
Braking resistor overload has timed out. This can be caused by
excessive braking resistor energy
no.PS No power board No communication between the power and control boards.
O.Ld1 Digital output overload The total current drawn from the AI-Adaptor 24 V supply or from
the digital output has exceeded the limit.
O.SPd Motor frequency has exceeded the
over frequency threshold
Excessive motor speed (typically caused by mechanical load
driving the motor).
Oh.dc DC bus over temperature DC bus component over temperature based on a software
thermal model.
Oht.C Control stage over-temperature Control stage over-temperature detected.
Oht.I Inverter over temperature based
on thermal model
IGBT junction over-temperature has been detected based on a
software thermal model.
Oht.P Power stage over temperature This trip indicates that a power stage over-temperature has
been detected.
OI.A1 Analog input 1 over-current Current input on analog input 1 exceeds 24 mA.
OI.AC Instantaneous output over current
detected
The instantaneous drive output current has exceeded.The set
limit.
Possible solutions:
• Increase acceleration/deceleration rate
• If seen during autotune reduce the voltage boost
• Check for short circuit on the output cabling
• Check integrity of the motor insulation using an insulation
tester
• Is the motor cable length within limits for the frame size
• Reduce the values in the current loop gain parameters
OI.br Braking IGBT over current
detected: short circuit protection
for the braking IGBT activated
Over current has been detected in braking IGBT or braking
IGBT protection has been activated.
Possible cause:
• Check brake resistor wiring
• Check braking resistor value is greater than or equal to the
minimum resistance value
• Check braking resistor insulation
OI.SC Output phase short-circuit Over-current detected on drive output when enabled.
Out.P Output phase loss detected Phase loss has been detected at the drive output.
OV DC bus voltage has exceeded the
peak level or maximum continuous
level for 15 seconds
The OV trip indicates that the DC bus voltage has exceeded the
maximum limit.
Possible solutions:
• Increase Deceleration Rate 1 (Pr 04)
• Decrease the braking resistor value (staying above the
minimum value)
• Check nominal AC supply level
• Check for supply disturbances which could cause the DC
bus to rise
• Check motor insulation using a insulation tester
P.dAt Power system configuration data
error
PAd Keypad has been removed The PAd trip indicates that the drive is in keypad mode and the
keypad has been disconnected from the drive.
Pb.bt Power board is in bootloader mode Power board is in bootloader mode
Pb.Er Communication has been lost /
errors detected between power
control
Communications loss between power and control.
Pb.HF Power board HF Power processor hardware fault - contact the supplier of the
drive
Pd.S Power down save error Error has been detected in the power down save parameters
saved in non-volatile memory.
PH.Lo Supply phase loss The drive has detected an input phase loss or large supply
imbalance.
PSU Internal power supply fault One or more internal power supply rails are outside limits or
overloaded.
r.All RAM allocation error Option module derivative image has requested more parameter
RAM than is allowed.
r.b.ht Hot rectifier/brake Over-temperature detected on input rectifier or braking IGBT.
rS Measured resistance has
exceeded the parameter range
The measured stator resistance during an autotune test has
exceeded the maximum possible value of Stator Resistance.
SCL Control word watchdog has timed
out
The control word has been enabled and has timed out
SL.dF Option module in option slot 1 has
changed
Option slot 1 on the drive is a different type to that installed
when parameters were last saved on the drive.
SL.Er Option module in option slot 1 has
detected a fault
Option module in option slot 1 on the drive has detected an
error
SL.HF Option module 1 hardware fault Option slot 1 on the drive has indicated a hardware fault.
SL.nF Option module in option slot 1 has
been removed
The option module in option slot 1 on the drive has been
removed since the last power up.
SL.tO Option module watchdog function
service error
The option module installed in Slot 1 has started the option
watchdog function and then failed to service the watchdog
correctly.
So.St Soft start relay failed to close, soft
start monitor failed
Soft start relay in the drive failed to close or the soft start
monitoring circuit has failed.
St.HF Hardware trip has occurred during
last power down
Hardware trip (HF01 –HF19) has occurred and the drive has
been power cycled. Enter 1299 to Pr 00 or xx.000 to clear trip
Sto No Safe Torque Off board fitted Internal STO board not fitted correctly.
th Motor thermistor over-temperature The motor thermistor connected to terminal 14 (digital input 5)
on the control connections has indicated a motor over
temperature.
th.br Brake resistor over temperature The th.br trip is initiated if the hardware based braking resistor
thermal monitoring is connected and the resistor overheats.
tH.Fb Internal thermistor has failed Internal thermistor has failed.
thS Motor thermistor short circuit The motor thermistor connected to terminal 14 (digital input 5)
on the control connections, is short circuit or low impedance
(<50 Ω).
tun.S Autotune test stopped before
completion
The drive was prevented from completing an autotune test,
because either the drive enable or the drive run signals were
removed.
tun.1 Autotune 1 The drive has tripped during a rotating autotune. The cause of
the trip can be identified from the sub-trip number.
Sub-trip-2 Reason=The motor did not reach the required speed during rotating auto-tune or mechanical load measurement.
tun.3 Autotune 3 RFC-A mode only.
The drive has tripped during a rotating auto-tune or mechanical
load measurement. The cause of the trip can be identified from
the associated sub-trip number
Sub-trip-1 Reason=Measured inertia has exceeded the parameter range during a mechanical
load measurement.
Sub-trip-3 Reason=The mechanical load test has been unable to identify the motor inertia
U.OI User OI ac The U.OI trip is initiated if the output current of the drive exceeds
the trip level set by User Over Current Trip Level. Refer to the
Control User Guide.
U.S User Save error / not completed The U.S trip indicates that an error has been detected in the user save parameters saved in non-volatile memory.
UP.uS User Program trip This trip can be initiated from within an onboard user program. Refer to the Control User Guide.
UPrG User Program An error has been detected in the onboard user program image.
Below list show nidec C200 drive alarm
Alarm string Description
br.res Brake resistor overload. Braking Resistor Thermal Accumulator in the drive has
reached 75.0 % of the value at which the drive will trip.Refer to the Power
Installation Guide.
OV.Ld Motor Protection Accumulator in the drive has reached 75.0 % of the value at
which the drive will trip and the load on the drive is >100 %, reduce motor current
(load). Refer to the Parameter Reference Guide
d.OV.Ld Drive over temperature. Percentage Of Drive Thermal Trip Level in the drive is
greater than 90 %. Refer to the Parameter Reference Guide
tuning The autotune procedure has been initialized and an autotune is in progress.
LS Limit switch active. Indicates that a limit switch is active and that is causing the
motor to be stopped
Lo.AC Low voltage mode. See Low AC Alarm in the Control User Guide
I.AC.Lt Current limit active. See Current Limit Active in the Control User Guide
24.LoSt t 24V backup not present. See 24V Alarm Loss Enable in the Control User Guide