Nidec & Control Techniques Commander C200, C300, NE200 & NE300 Drive
1
Posts
1
Users
0
Reactions
133
Views
Apr 08, 2024 5:23 am
Cause : Control stage over temperature- This trip indicates that a control stage over-temperature has been detected if Cooling Fan control (06.045) = 0.
- Increase ventilation by setting Cooling Fan control (06.045) > 0.
- This trip causes the option module to go to standby and Potential Drive Damage Conditions (10.106) bit 1 to be set.