Cause : Power stage over temperature comes when a power stage over-temperature has been detected. From the sub-trip ‘xxyzz’, the Thermistor location is identified by ‘zz’.
- Check enclosure / drive fans are still functioning correctly.
- Force the heatsink fans to run at maximum speed.
- Check enclosure ventilation paths.
- Check enclosure door filters.
- Increase ventilation.
- Reduce the drive switching frequency.
- Reduce duty cycle.
- Increase acceleration / deceleration rates.
- Use S-ramp (Pr 02.006).
- Reduce motor load.
- Check the derating tables and confirm the drive is correctly sized for the application.
- Use a drive with larger current / power rating.