Cause : Instantaneous output over current detected comes when the instantaneous drive output current has exceeded VM_DRIVE_CURRENT_MAX. This trip cannot be reset until 10 s after the trip was initiated.
- Increase acceleration/deceleration rate.
- If seen during auto-tune reduce the voltage boost.
- Check for short circuit on the output cabling.
- Check integrity of the motor insulation using an insulation tester.
- Is the motor cable length within limits for the frame size.
- Reduce the values in the frequency loop gain parameters - (Pr 03.010, 03.011, 03.012) or (Pr 03.013, 03.014, 03.015).
- Reduce the values in the current loop gain parameters.