OI.SC fault error 228 in commander C200 nidec control techniques drive

1 Posts
1 Users
0 Reactions
190 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Output phase short-circuit comes when over-current detected on drive output when enabled. Possible motor earth fault.

  1. Check for short circuit on the output cabling.
  2. Check integrity of the motor insulation using an insulation tester.
  3. Is the motor cable length within limits for the frame size?