Cause : Measured resistance has exceeded the parameter range comes when the rS trip indicates that the measured stator resistance of the motor during an auto-tune test has exceeded the maximum possible value of Stator Resistance (05.017).
- If the measured value or a value written to this parameter by the user exceeds (VFS /√2) / Full Scale Current Kc (11.061).
- Ensure the stator resistance of the motor falls within the range of the drive model. The most likely cause of this trip is trying to measure a motor much smaller than the drive rating. Ratio’s of drive size to motor size of greater than 15:1 are likely to lead to a problem.
- Check that a value has not been entered in the stator resistance for the presently selected motor map that exceeds the allowed range.
- Check the motor cable / connections.
- Check the integrity of the motor stator winding using an insulation tester.
- Check the motor phase to phase resistance at the drive terminals.
- Check the motor phase to phase resistance at the motor terminals.
- Ensure the stator resistance of the motor falls within the range of the drive model.
- Select fixed boost mode (Pr 05.014 = Fd) and verify the output current waveforms with an oscilloscope.
- Replace the motor.