Forum

Share:
Notifications
Clear all

SPO fault code in NE300 nidec control techniques drive

1 Posts
1 Users
0 Reactions
322 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Output phase loss comes when open phase is present in the motor or when you run drive without motor. An "output phase loss fault" typically refers to a situation where one of the phases in the output of a three-phase electrical system is lost or disconnected.

  1. A loose connection or splice is present.
  2. An external device between the motor and drive has failed.
  3. An open phase is present in the motor.
  4. Check U-V-W motor wiring.
  5. Check the load.
Share: