th.br fault error 10 in commander C200 nidec control techniques drive

1 Posts
1 Users
0 Reactions
183 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Brake resistor over temperature comes when the th.br trip is initiated if the hardware based braking resistor thermal monitoring is connected and the resistor overheats.

  1. If the braking resistor is not used, then this trip must be disabled with bit 3 of Action On Trip Detection (10.037) to prevent this trip.
  2. Check brake resistor wiring.
  3. Check braking resistor value is greater than or equal to the minimum resistance value.
  4. Check braking resistor insulation.