C.rtg fault 186 in unidrive SP nidec control techniques drive

1 Posts
1 Users
0 Reactions
88 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : SMARTCARD trip- The voltage and/or current rating of the source and destination drives are different. Drive rating dependent parameters (parameters with the RA coding) are likely to have different values and ranges with drives of different voltage and current ratings.

  1. Parameters with this attribute will not be transferred to the destination drive by SMARTCARDs when the rating of the destination drive is different from the source drive and the file is a parameter file.
  2. However, with software V01.09.00 and later drive rating dependent parameters will be transferred if only the current rating is different and the file is a differences from default type file.