Forum

Share:
Notifications
Clear all

E003 fault error in commander S100 control techniques drive

1 Posts
1 Users
0 Reactions
583 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Over Current comes when the instantaneous drive output current has exceeded the over current threshold of the drive. This error cannot be reset until 10 s after it was initiated.

  1. Increase time taken for the drive to accelerate/decelerate.
  2. Check for short circuit on the output cabling.
  3. Check integrity of the motor insulation using an insulation tester.
  4. Check the motor cable length is within limits of the drive.
  5. Reduce the value set in Current Loop Gain (P3.23).
Share: