Forum
Share:
Notifications
Clear all
E028 fault error in commander S100 control techniques drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
Cause : An In 1 Current comes when a current loss was detected in T2 analog input 1 and the input type is set to 4-20 mA Error (6). Loss of input is detected if the current falls below 3 mA.
  1. Check control wiring is correct.
  2. Check control wiring is undamaged.
  3. Check T2 Analog Input 1 Type (P6.01).
  4. Check the current signal is present and greater than 3 mA.
Share: