Cause : An In 1 Current comes when a current loss was detected in T2 analog input 1 and the input type is set to 4-20 mA Error (6). Loss of input is detected if the current falls below 3 mA.
- Check control wiring is correct.
- Check control wiring is undamaged.
- Check T2 Analog Input 1 Type (P6.01).
- Check the current signal is present and greater than 3 mA.