Cause : An In 2 Current comes when a current loss was detected in T4 analog input 2 and the input type is set to 4-20 mA Error (6). Loss of input is detected if the current falls below 3 mA.
- Check control wiring is correct.
- Check control wiring is undamaged.
- Check T4 Analog Input 2 Type (P6.02).
- Check the current signal is present and greater than 3 mA.