Nidec & Control Techniques Commander S, SE, SX, SK & SP Drive
846
Apr 05, 2024 12:07 pm
Cause : Drive encoder trip- Servo mode phasing failure because encoder phase angle (Pr 3.25 or Pr 21.20) is incorrect.
- Check the encoder wiring.
- Perform an autotune to measure the encoder phase angle or manually enter the correct phase angle into Pr 3.25 (or Pr 21.20).
- Spurious Enc10 trips can be seen in very dynamic applications.
- This trip can be disabled by setting the overspeed threshold in Pr 3.08 to a value greater than zero.
- Caution should be used in setting the over speed threshold level as a value which is too large may mean that an encoder fault will not be detected