Cause : Drive encoder trip- Wire break (Drive encoder terminals 1 & 2, 3 & 4, 5 & 6). If wire break detection on the main drive encoder input is not required, set Pr 3.40 = 0 to disable the Enc2 tri.

  1. Check cable continuity.
  2. Check wiring of feedback signals is correct.
  3. Check encoder power supply is set correctly in Pr 3.36 Replace feedback device.