Nidec & Control Techniques Commander S, SE, SX, SK & SP Drive
1
Posts
1
Users
0
Reactions
539
Views
Apr 05, 2024 11:58 am
Cause : Drive encoder trip- Wire break (Drive encoder terminals 1 & 2, 3 & 4, 5 & 6). If wire break detection on the main drive encoder input is not required, set Pr 3.40 = 0 to disable the Enc2 tri.
- Check cable continuity.
- Check wiring of feedback signals is correct.
- Check encoder power supply is set correctly in Pr 3.36 Replace feedback device.