Cause : Braking resistor overload timed out (I 2 t) – accumulator value can be seen in Pr 10.39. Ensure the values entered in Pr 10.30 and Pr 10.31 are correct.

  1. Increase the power rating of the braking resistor and change Pr 10.30 and Pr 10.31.
  2. If an external thermal protection device is being used and the braking resistor software overload is not required, set Pr 10.30 or Pr 10.31 to 0 to disable the trip.