OIAC.P fault in unidrive SP nidec control techniques drive

1 Posts
1 Users
0 Reactions
248 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Power module over current detected from the module output currents comes when the drive detects that the current flowing through the motor exceeds the preset limits.

  1. Acceleration /deceleration rate is too short.
  2. If seen during autotune reduce voltage boost Pr 5.15.
  3. Check for short circuit on output cabling.
  4. Check integrity of motor insulation.
  5. Check feedback device wiring.
  6. Check feedback device mechanical coupling.
  7. Check feedback signals are free from noise.