OSP fault code in commander SX control techniques drive
Cause : Over speed comes when the LOAD is pushing the MOTOR, instead of the other way around. Motor is turning faster than highest allowed speed due to incorrectly set minimum/maximum speed, insufficient braking torque.
  1. The speed is higher than 1.2 times the value of 00 22
  2. Check that the load is not driving.
  3. Check that the overspeed threshold has been set correctly.
  4. Adjust the speed loop gains.
  5. Set a longer deceleration time.