Cause : Overvoltage comes when DC bus voltage has exceeded the peak level or the maximum continuous level for 15 seconds.
- Increase deceleration ramp (Pr 0.04).
- Decrease braking resistor value (staying above the minimum value).
- Check nominal AC supply level.
- Check for supply disturbances which could cause the DC bus to rise – voltage overshoot after supply recovery from a notch induced by DC drives.
- Check motor insulation.