Cause : Phase loss comes when one of the input phases has become disconnected from the drive. High input voltage phase imbalance or input phase loss.

  1. Normally a motor load of between 50 and 100% of drive rating is required to trigger the trip.
  2. The drive will attempt to stop the motor before tripping.
  3. The drive looks at DC Bus ripple.