Cause : Analog input 2 current loss comes when an Input 2 Loss indicates that a current loss was detected in current mode on Analog input 2 (Terminal 7). In 4-20 mA and 20-4 mA modes loss of input is detected if the current falls below 3 mA.

1. Check control wiring is correct
2. Check control wiring is undamaged
3. Check the Analog Input 2 Mode (07.011)
4. Current signal is present and greater than 3 mA