Card Boot fault in nidec control techniques drive
Cause : The Menu 0 parameter modification cannot be saved to the NV Media Card comes when menu 0 changes are automatically saved on exiting edit mode.
  1. The Card Boot trip will occur if a write to a Menu 0 parameter has been initiated via the keypad by exiting edit mode
    and Pr 11.042 is set for auto or boot mode, but the necessary boot file has not been created on the NV Media Card to take the new parameter value.
  2. This occurs when Pr 11.042 is changed to Auto (3) or Boot (4) mode, but the drive is not subsequently reset.
  3. The action of resetting the trip will create the necessary file and prevent further trips.
  4. Ensure that Pr 11.042 is correctly set, and then reset the drive to create the necessary file on the NV Media Card.
  5. Re-attempt the parameter write to the Menu 0 parameter.