Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
414
Apr 12, 2024 11:58 am
Cause : NV Media Card trip; option modules installed are different between source drive and destination drive comes when the Card Option trip indicates that parameter data or default difference data is being transferred from a NV Media Card to the drive, but the option module categories are different between source and destination drives.
- This trip does not stop the data transfer, but is a warning that the data for the option modules that are different will be set to the default values and not the values from the card.
- This trip also applies if a compare is attempted between the data block and the drive.
- Ensure the correct option modules are installed.
- Ensure the option modules are in the same option module slot as the parameter set stored.
- Press the red reset button to acknowledge that the parameters for one or more of the option modules installed will be at their default values.
- This trip can be suppressed by setting Pr mm.000 to 9666 and resetting the drive.