Card Product fault in nidec control techniques drive
Cause : NV Media Card data blocks are not compatible with the drive derivative comes when Drive Derivative (11.028) or Product Type (11.063) are different between the source and target drives then this trip is initiated either at power-up or when the card is accessed.
It will have one of the following sub-trip numbers:
1 - If Drive Derivative (11.028) is different between the source and target drives, this trip is initiated either at power-up or when the SD Card is accessed. Data is still transferred, since this is a warning trip; the trip can be suppressed by entering code 9666 in parameter xx.000, and resetting the drive (this applies the warning suppression flag to the card).
2 - If Product Type (11.063) is different between the source and target drives or if corruption is detected in the parameter file, this trip is initiated either at power-up or when the SD Card is accessed. This trip can be reset but no data are transferred in either direction between the drive and the card.
3 - A Unidrive SP parameter value was found that has no equivalent parameter on the destination drive. Data is still transferred, since this is a warning trip; the trip can be suppressed by entering code 9666 in Pr xx.000, and resetting the drive (this applies the warning suppression flag to the card).
Use a different NV Media Card. This trip can be suppressed by setting Pr mm.000 to 9666 and resetting the drive.