Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
226
Apr 12, 2024 12:01 pm
Cause : NV Media Card Trip- The voltage and / or current rating of the source and destination drives are different comes when the Card Rating trip indicates that parameter data is being transferred from a NV Media Card to the drive, but the current and / or voltage ratings are different between source and destination drives.
- This trip also applies if a compare (using Pr mm.000 set to 8yyy) is attempted between the data block on a NV Media Card and the drive.
- The Card Rating trip does not stop the data transfer but is a warning that rating specific parameters with the RA attribute may not be transferred to the destination drive.
- Reset the drive to clear the trip.
- Ensure that the drive rating dependent parameters have transferred correctly.
- This trip can be suppressed by setting Pr mm.000 to 9666 and resetting the drive.