Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
797
Apr 12, 2024 12:17 pm
Cause : Drive position feedback interface power supply overload comes when the Encoder 1 trip indicates that the drive encoder power supply has been overloaded. Terminals 13 &14 of the 15 way D type connector can supply a maximum current of 200 mA @ 15 V or 300 mA @ 8 V and 5 V.
- Check encoder power supply wiring.
- Disable the termination resistors (Pr 03.039 set to 0) to reduce current consumption.
- For 5 V encoders with long cables, select 8 V (Pr 03.036) and install a 5 V voltage regulator close to the encoder.
- Check the encoder specification to confirm if it is compatible with the encoder port power supply current capability.
- Replace the encoder.
- Use an external power supply with higher current capability.