Cause : Data read from the encoder is out of range during auto-configuration comes when the Encoder 13 trip indicates that the data read from the encoder was out of the range during auto-configuration. No parameters will be modified with the data read from the encoder as a result of auto configuration.
The tens in the sub-trip number indicate the interface number (i.e. 1 for P1 interface and 2 for P2 interface). Sub-trip & Reason given below:
x1 - Rotary lines per revolution error.
x2 - Linear comms pitch error.
x3 - Linear line pitch error.
x4 - Rotary turns bits error.
x5 - Communications bits error.
x6 - Calculation time is too long.
x7 - Line delay measured is longer than 5 μs.
Enter the encoder setup parameters manually. Check to see the encoder supports auto-configuration.