Cause : The data given in the additional configuration parameter for a position feedback interface is out of range comes when the Encoder 14 trip indicates that the data given in the additional configuration parameter for a position feedback interface is out of range.
If the sub-trip number is one then the data is out of range in P1 Additional Configuration (03.074), or if the sub-trip number is 2 the data is out of range in P2 Additional Configuration (03.174). Not all position feedback devices use
the additional configuration, but those that do are listed below:
Range checking is applied to the turns padding (decimal digits 5-3) and position padding (decimal digits 2-0). If these give a padding value outside +/-16 then the trip is initiated. Note that in each case the most significant digit indicates left (0) or right (1) padding, and the least significant 2 digits indicate the number of bits.