Encoder 14 fault in nidec control techniques drive

1 Posts
1 Users
0 Reactions
96 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The data given in the additional configuration parameter for a position feedback interface is out of range comes when the Encoder 14 trip indicates that the data given in the additional configuration parameter for a position feedback interface is out of range.

If the sub-trip number is one then the data is out of range in P1 Additional Configuration (03.074), or if the sub-trip number is 2 the data is out of range in P2 Additional Configuration (03.174). Not all position feedback devices use
the additional configuration, but those that do are listed below:

Range checking is applied to the turns padding (decimal digits 5-3) and position padding (decimal digits 2-0). If these give a padding value outside +/-16 then the trip is initiated. Note that in each case the most significant digit indicates left (0) or right (1) padding, and the least significant 2 digits indicate the number of bits.