Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
335
Apr 12, 2024 12:33 pm
Cause : Checksum or CRC error comes when the Encoder 5 trip indicates that there is a checksum or CRC error, or the SSI encoder is not ready. The Encoder 5 trip can also indicate a wire break to a communications based encoder.
- Check the encoder cable shield connections.
- Ensure the cable is one uninterrupted cable - remove any connector blocks or if unavoidable minimise the length of any shield pigtails to the connector block.
- Check the encoder signal for noise with an oscilloscope.
- Check the comms resolution setting (Pr 03.035).
- If using a Hiperface, EnDat encoder carry out an encoder auto-configuration (Pr 03.041 = Enabled).
- Replace the encoder.