Motor Too Hot fault in nidec control techniques drive

1 Posts
1 Users
0 Reactions
476 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Output current overload timed out (I2 t) comes when the Motor Too Hot trip indicates a motor thermal overload based on the Rated Current (Pr 05.007) and Motor Thermal Time Constant (Pr 04.015). Pr 04.019 displays the motor temperature as a percentage of the maximum value.

  1. The drive will trip on Motor Too Hot when Pr 04.019 gets to 100 %.
  2. Ensure the load is not jammed / sticking.
  3. Check the load on the motor has not changed.
  4. If seen during an auto-tune test in RFC-S mode, ensure the motor Rated Current in Pr 05.007 is ≤ Heavy duty current rating of the drive.
  5. Tune the Rated Speed (Pr 05.008) (RFC-A mode only).
  6. Check feedback signal for noise.
  7. Ensure the motor rated current is not zero.
  8. This trip can be disabled and current limiting activated on the motor overload by setting thermal protection mode Pr 04.016 to 1.