Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
757
Apr 13, 2024 5:10 am
Cause : DC bus over temperature- The OHt dc bus trip indicates a DC bus component over temperature based on a software thermal model. The drive includes a thermal protection system to protect the DC bus components within the drive.
- This includes the effects of the output current and DC bus ripple.
- The estimated temperature is displayed as a percentage of the trip level in Pr 07.035.
- If this parameter reaches 100 % then an OHt dc bus trip with sub-trip 200 is initiated.
- The drive will attempt to stop the motor before tripping.
- If the motor does not stop in 10 seconds the drive trips immediately.
- Check the AC supply voltage balance and levels.
- Check DC bus ripple level.
- Reduce duty cycle.
- Reduce motor load.
- Check the output current stability.