OHt Inverter fault in nidec control techniques drive

1 Posts
1 Users
0 Reactions
495 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Inverter over temperature based on thermal model comes when an IGBT junction over-temperature has been detected based on a software thermal model.

The sub- trip indicates which model has initiated the trip in the form xxyzz as given below:

Source xx y zz Description
Control system 0 1 0 Inverter thermal model
Control system 0 3 0 Braking IGBT thermal model
  1. Reduce the selected drive switching frequency.
  2. Ensure Auto-switching Frequency Change Disable (05.035) is set to Off.
  3. Reduce duty cycle.
  4. Increase acceleration / deceleration rates.
  5. Reduce motor load.
  6. Check DC bus ripple.
  7. Ensure all three input phases are present and balanced.