Cause : Power stage over temperature - This trip indicates that a power stage over-temperature has been detected.

From the sub-trip ‘xxyzz’, the Thermistor location which is indicating the over-temperature is identified by ‘zz’.The thermistor numbering is different for a single module type drive (i.e. no parallel board fitted) and a multi-module type drive (i.e. parallel board fitted with one or more power modules) as shown below:

Single module type drive:

Source xx y zz Description
Power system 1 0 zz Thermistor location defined by zz in the power board
Power system 1 Rectifier number zz Thermistor location defined by zz in the rectifier

Multi-module type system:

Source xx y zz Description
Power system power module number 0 1 U phase power device
Power system power module number 0 2 V phase power device
Power system power module number 0 3 W phase power device
Power system power module number 0 4 Rectifier
Power system power module number 0 5 General power system
Power system power module number 0 0 Braking IGBT
  1. Check enclosure / drive fans are still functioning correctly.
  2. Force the heatsink fans to run at maximum speed.
  3. Check enclosure ventilation paths.
  4. Check enclosure door filters.
  5. Increase ventilation.
  6. Reduce the drive switching frequency.
  7. Reduce duty cycle.
  8. Increase acceleration / deceleration rates.
  9. Use S ramp (Pr 02.006).
  10. Reduce motor load.
  11. Check the derating tables and confirm the drive is correctly sized for the application.