Nidec & Control Techniques Unidrive M700, M600, M400, HS30 & HS70 Drive
1
Posts
1
Users
0
Reactions
1,074
Views
Apr 13, 2024 5:19 am
Cause : Instantaneous output over current detected comes when the instantaneous drive output current has exceeded VM_DRIVE_CURRENT[MAX]. This trip cannot be reset until 10 s after the trip was initiated.
- Acceleration/deceleration rate is too short.
- If seen during auto-tune reduce the voltage boost.
- Check for short circuit on the output cabling.
- Check integrity of the motor insulation using an insulation tester.
- Check feedback device wiring.
- Check feedback device mechanical coupling.
- Check feedback signals are free from noise.
- Is motor cable length within limits for the frame size.