User 24V fault in nidec control techniques drive

1 Posts
1 Users
0 Reactions
198 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : User 24 V supply is not present on control terminals (1,2) comes when a User 24 V trip is initiated, if User Supply Select (Pr 06.072) is set to 1 or Low Under Voltage Threshold Select (06.067) = 1 or Backup Supply Mode Enable (06.068) = 1 and no user 24 V supply is present on control terminals 1 and 2.

  • Ensure the user 24 V supply is present on control terminals 1 (0V) and 2 (24V).