75
Apr 29, 2025 10:15 am
Cause : AMBIENT TEMP comes when the ambient temperature in the drive is too high. This limit is set to protect the drive's internal components from overheating, which can lead to reduced performance or even damage.
AOT AMBIENT TEMP fault in Parker AC890 drive indicate that the ambient temperature surrounding the drive has exceeded a predefined limit.
High Ambient Temperature:
- Solution: Check the surrounding environment for heat sources like direct sunlight, nearby machinery, or insufficient ventilation. If possible, relocate the drive to a cooler area.
- Consider: Installing cooling fans or air conditioning to reduce the ambient temperature.
Ventilation Issues:
- Solution: Ensure that the drive has adequate ventilation. Check for obstructions that might be blocking airflow, such as dust, dirt, or nearby objects. Clean the drive and remove any obstructions.
- Consider: Installing additional fans or vents to improve airflow.
Drive Overloading:
- Solution: Verify that the drive is not being overloaded. Check the load on the drive and ensure it doesn't exceed its rated capacity. If necessary, reduce the load or consider upgrading to a more powerful drive.
Internal Component Failure:
- Solution: If none of the above solutions resolve the issue, it might be due to a faulty internal component within the drive. Consult the drive's manual or contact Parker's technical support for further troubleshooting or replacement options.