Cause : FEEDBACK MISSING comes when the drive has been configured to run in Closed Loop Vector control mode with a Pulse Encoder IO Option, but the IO Option has not been correctly configured.

FEEDBACK MISSING fault in a Parker AC30 drive indicates that the drive is not receiving feedback signals from a connected sensor, such as an encoder or resolver. This can prevent the drive from accurately controlling the motor's speed or position.

Common Causes of FEEDBACK MISSING Faults:

  • Sensor Issues:
    • Faulty sensor
    • Damaged or loose wiring to the sensor
    • Incorrect sensor configuration
  • Drive Configuration Errors:
    • Incorrect feedback signal type or parameters configured in the drive
    • Communication problems between the drive and the sensor
  • External Factors:
    • Power supply issues
    • Environmental factors (e.g., temperature, humidity)

Troubleshooting Steps:

  1. Verify Sensor Connection:
    • Ensure that the sensor is properly connected to the drive and that the cables are secure.
    • Check for any signs of damage or corrosion in the cables.
  2. Test the Sensor:
    • Use a multimeter or diagnostic tool to test the sensor's output signal.
    • Compare the measured values to the expected specifications.
  3. Review Drive Configuration:
    • Verify that the feedback signal type and parameters are correctly configured in the drive.
    • Check for any errors or warnings related to feedback in the drive's status messages.
  4. Check Power Supply:
    • Ensure that the power supply is providing the correct voltage and current to the sensor.