MAG CURRENT FAIL fault in parker AC690 drive comes when it was not possible to find a suitable value of magnetising current to achieve the required operating condition for the motor.
- Check the motor data is correct, especially nameplate rpm and motor volts.
- Also check that the motor is correctly rated for the drive.