Parker AC890 drive fault codes
Comprehensive list of common fault codes for Parker AC890 series AC drives, including causes, troubleshooting steps, and safety considerations. Quickly diagnose and resolve drive issues to minimize downtime.
Below list shows fault codes and their solutions of Parker AC890 drive fault codes:
6511
Keypad Display
6901
Keypad Display
Description
Possible Reason for Trip
DCHI
OVERVOLTAGE
The drive internal dc link voltage is too high
¨    The supply voltage is too high
¨    Trying to decelerate a large inertia load too quickly
¨    The brake resistor is open circuit
DCLO
UNDERVOLTAGE
The drive internal dc link voltage is too low
¨    The supply voltage is too low
¨    The supply has been lost
¨    A supply phase is missing
OC
OVERCURRENT
The motor current being drawn from the drive is too high
¨    Trying to accelerate a large inertia load too quickly
¨    Application of shock load to motor
¨    Short circuit between motor phases
¨    Short circuit between motor phase and earth
¨    Motor output cables too long or too many parallel motors connected to the drive
¨    Fixed or auto boost levels are set too high
STO
SAFE TORQUE OFF
Safe Torque Off (STO) is active.
¨    One or both STO user inputs is low
¨    A fault has been detected in the STO circuit
HOT
HEATSINK
The drive heatsink temperature is too high
¨    The ambient air temperature is too high
¨    Poor ventilation or spacing between drives
ET
EXTERNAL TRIP
User trip caused via control terminals
¨ +24V not present on external trip (terminal X15/05)
¨    Check setting of EXT TRIP MODE parameter
IN 1
INPUT 1 BREAK
I/O TRIPS:: INPUT 1
BREAK has gone True
¨    Check configuration to determine source of signal
IN 2
INPUT 2 BREAK
I/O TRIPS:: INPUT 2
BREAK has gone True
STLL
MOTOR STALLED
The motor has stalled (not rotating)
¨    Motor loading too great
¨    Current limit level is set too low
¨    Stall trip duration is set too low
IT
INVERSE TIME
¨    The inverse time current limit is active: motor loading is too great; fixed or auto boost levels are too high (Full Load Current = 150% for 60 seconds)
DB R
BRAKE RESISTOR
External dynamic braking resistor has been overloaded
¨    Trying to decelerate a large inertia load too quickly or too often
DB S
BRAKE SWITCH
Internal dynamic braking switch has been overloaded
DISP
OP STATION
Keypad has been disconnected from drive whilst drive is running in local control
¨    Keypad accidentally disconnected from drive
SCI
COMMS BREAK
¨    COMMS BREAK parameter set to True (refer to I/O TRIPS menu at level 3)
CNTC
CONTACTOR FBK
¨    The CONTACTOR CLOSED input in the SEQUENCING LOGIC function block remained FALSE after a run command was issued
SPD
SPEED FEEDBACK
¨    SPEED ERROR > 50.00% for 10 seconds
AOT
AMBIENT TEMP
¨    The ambient temperature in the drive is too high
OT
MOTOR OVERTEMP
The motor temperature is too high
¨    Excessive load
¨    Motor voltage rating incorrect
¨    FIXED BOOST and/or AUTO BOOST set too high
¨    Prolonged operation of the motor at low speed without forced cooling
¨    Check setting of INVERT THERMIST parameter in I/O TRIPS menu at level 3.
¨    Break in motor thermistor connection
I HI
CURRENT LIMIT
V/Hz mode only: If the current exceeds 180% of induction stack rated current for a period of 1 second, the drive will trip. This is caused by shock loads
¨    Remove the cause of the shock load
A24SC
24V FAILURE
The 24V customer output has fallen below 17V
¨    24V customer output is short circuited
¨    Excessive loading
LSPD
LOW SPEED OVER I
The motor is drawing too much current (>100%) at zero output frequency
¨    FIXED BOOST and/or AUTO BOOST set too high (refer to FLUXING menu at level 3)
PHAS
PHASE FAIL
¨    One or more input phases not present
ENC 1
FBK ENCODER FAIL
¨    Encoder fault
SHRT
DESAT (OVER I)
¨    Instantaneous overcurrent. Refer to OVERCURRENT in this table
DCRP
VDC RIPPLE
¨    The dc link ripple voltage is too high. Check for a missing input phase.
DBSC
BRAKE SHORT CCT
Brake resistor overcurrent
¨    Check brake resistance is not less than minimum value allowed
¨    check wiring and brake resistor for earth faults
OSPD
OVERSPEED
¨    Speed feedback > 150% for 0.1 seconds
ANIN
ANALOG INPUT ERR
¨    4-20mA analog input current > 22mA could damage the input circuit
DBCT
INT DB RESISTOR
¨    Braking mode set to INTERNAL (future use only). Set to EXTERNAL and connect an External Braking Resistor if braking is required.
TRIP
UNKNOWN
¨    An unknown trip - refer to Parker Hannifin Manufacturing
TR32
OTHER
¨    Refer to OTHER in Appendix D: TRIPS STATUS. One or more trips have occurred with a Value greater than 32. See the list.
ATN1
MAX SPEED LOW
¨    During Autotune the motor is required to run at the nameplate speed o f the motor. If MAX SPEED RPM limits the speed to less than this value, an error will be reported. Increase the value of MAX SPEED RPM up to the nameplate rpm of the motor (as a minimum). It may be reduced, if required, after the Autotune is complete.
ATN2
MAINS VOLTS LOW
¨    The mains input voltage is not sufficient to carry out the Autotune. Re-try when the mains have recovered.
ATN 3
NOT AT SPEED
¨    The motor was unable to reach the required speed to carry out the Autotune. Possible reasons include: motor shaft not free to turn; the motor data is incorrect
ATN4
MAG CURRENT FAIL
¨    It was not possible to find a suitable value of magnetising current to achieve the required operating condition for the motor. Check the motor data is correct, especially nameplate rpm and motor volts. Also check that the motor is correctly rated for the drive.
ATN5
NEGATIVE SLIP F
¨    Autotune has calculated a negative slip frequency, which is not valid. Nameplate rpm may have been set to a value higher than the base speed of the motor. Check nameplate rpm, base frequency, and pole pairs are correct.
ATN6
TR TOO LARGE
¨    The calculated value of rotor time constant is too large. Check the value of nameplate rpm.
ATN7
TR TOO SMALL
¨    The calculated value of rotor time constant is too small. Check the value of nameplate rpm.
ATN8
MAX RPM DATA ERR
¨    This error is reported when the MAX SPEED RPM is set to a value outside the range for which Autotune has gathered data. Autotune gathers data on the motor characteristics up to 30% beyond “max speed rpm”. If MAX SPEED RPM is later increased beyond this range, the drive had no data for this new operating area, and so will report an error. To run the motor beyond this point it is necessary to re-autotune with MAX SPEED RPM set to a higher value.
STAC
STACK TRIP
¨    The drive was unable to distinguish between an overcurrent/desat or overvoltage trip
ATNA
LEAKGE L TIMEOUT
¨    The leakage inductance measurement requires a test current to be inserted into the motor. It has not been possible to achieve the required level of current. Check that the motor is wired correctly.
PLOS
POWER LOSS STOP
¨    Power Loss Stop sequence has ramped Speed Setpoint to zero or timed out
ATNC
MOTR TURNING ERR
¨    The motor must be stationary when starting the Autotune
ATND
MOTR STALLED ERR
¨    The motor must be able to rotate during Autotune
ATNE
AT TORQ LIM ERR
¨    The motor is in torque limit during Autotune
ECAL
FBK ENCODR CAL
The drive has failed to set absolute position
¨    Check the encoder supports absolute position, and that the encoder is wired correctly.
GEAR
OUTPUT GBX ERROR
¨    A non-unity output gearbox is not supported if the encoder direction is reversed.
APP
APP HALTED
¨    The application has been halted by the DSE Configuration Tool
AERR
APP ERROR
¨    The application has ceased execution due to an error
FERR
FIRMWARE ERROR
¨    The firmware in the drive has stopped executing
RSLV
RESOLVER ERROR
See function block description
¨    Resolver disconnected
¨    Resolver incorrectly wired
¨    Resolver not compatible with resolver feedback option board
¨    Resolver length cable too long
¨    Incorrect Resolver Function Block settings
MI2T
I2T MOTOR TRIP
¨    Motor is undersized
STO
SAFE TORQUE OFF
¨    The safe torque off feature has been activated. See Chapter 6, STO Trip Annunciation.
REFC
REF ENCODER CAL
REFF
REF ENCODER FAIL
¨    Function not implemented
DCFG
DRIVE CONFIG ERR
Drive configuration error
¨    The configuration defined in DRIVE CONFIG doesn't match the actual drive configuration.
CT1
CUST TRIP 1
CT2
CUST TRIP 2
CT3
CUST TRIP 3
CT4
CUST TRIP 4
CT5
CUST TRIP 5
CT6
CUST TRIP 6
CT7
CUST TRIP 7
DCHI
OVERVOLTAGE
The shared dc link voltage is too high
Trying to decelerate a large inertia load too quickly The brake resistor is open circuit
OC
OVERCURRENT
The current being drawn from the drive is too high
HOT
HEATSINK
The heatsink temperature is too high
IT
INVERSE TIME
High output current for prolonged period, (warning only)
DISP
DISPLAY / KEYPAD
Loose connection to display
SCI
LOST COMMS
Not used
T   6
24V FAILURE
T   4
VOLTS SEL SWITCH
Failure to read voltage selector switch
May be caused by excessive loading on ANOUT
PHAS
PHASE LOSS
CHRG
CHARGING
Failed to charge DC link
Excessive capacitance on DC link
Short circuit on DC link
DCRP
VDC RIPPLE
Excessive DC link ripple
Driving a reciprocating load
AOUT
ANOUT FAULT
Overload on analog output
VOLT
VOLTS SELECTION
Invalid position on volts selector switch
ENCI
ENC NEEDS INIT
PMAC motor used with a relative encoder – Needs to run init once per power cycle
Relative encoder needs to be aligned with the motor back EMF. Use MOT POLARISATION feature to align
COMMS FAULT
CODE N
The drive has not responded to a message from the 6901
Drive CPU busy.
COMMS FAULT
CODE C
Incorrect reply from drive following a selection (command) message from the 6901
COMMS FAULT
CODE P
Parity error in message received from the drive by the 6901
COMMS FAULT
CODE F
Format of message received from the drive by the 6901 is incorrect
Unexpected, due to electrical interference
BCC (block check character) in message received from the drive by the 6901 is incorrect
COMMS FAULT CODE B
COMMS FAULT
CODE L
Length of message received from the drive by the 6901 is incorrect (too many characters)