PMAC SPEED ERROR fault in parker AC30 drive

1 Posts
1 Users
0 Reactions
39 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : PMAC SPEED ERROR comes when a discrepancy between the commanded speed and the actual motor speed. When using the Start feature in Sensorless Vector Control, the real speed hasn’t reached the speed setpoint after 5 seconds to move from open to closed loop control or to move from closed to open loop.