QUICKSTOP ACTIVE fault in parker AC30 drive - This fault comes when attempting to start the drive in local mode with Quick Stop active.
- The Quick Stop input is active low.
- This input needs to be driven high.
- The input may be ignored in the standard application by setting “Disable Quick Stop”.