KV5500 Specifications
Power voltage
24 VDC (±10%)
Operating ambient temperature
0 to +50°C (with no frost)*1*2
Operating ambient humidity
10 to 95%RH (no condensation)*3
Ambient temperature for storage
-20 to +70°C*3
Storage relative humidity
10 to 95 % RH (No condensation)*1*4
Operating environment
Without dust and corrosive gas
Altitude
2,000 m or less
Noise immunity
1,500 Vp-p or more, pulse width: 1 µs, 50 ns (by way of a noise simulator)
Withstand voltage
1,500 VAC for 1 minute between the power supply terminal and the I/O terminals and between all the external terminals and the case
Insulation resistance
50 MΩ or more (tested with a 500 VDC megger, between the power supply terminal and the I/O terminals and between all the external terminals and the case)
Shock resistance
Acceleration 150 m/s2, Operation time 11 ms, twice in each of the X, Y and Z directions
Overvoltage category
II (when using KV-U7)
Pollution degree
2
Vibration resistance
Intermittent vibration
Frequency 5 to 9 Hz
Half amplitude: 3.5 mm
Frequency 9 to 150 Hz
Acceleration: 9.8 m/s2
Continuous vibration
Frequency 5 to 11 Hz
Half amplitude: 1.75 mm
Acceleration: 4.9 m/s2
Arithmetic control mode
Stored program mode
I/O control mode
Refresh mode
Program language
Expanded ladder, KV Script, mnemonic
Number of commands
Basic instruction: 81 classes, 182 instructions
Applied instruction: 42 classes, 59 instructions
Arithmetic operation instruction: 124 classes, 315 instructions
Extended instruction: 124 classes, 315 instructions
Total: 345 classes, 703 instructions
Instruction execution speed
Basic instruction: Min. 10 ns
Applied instruction: Min. 20 ns
Double precision floating-point instruction: Min. 2,350 ns
Program capacity
Approx. 260k steps
Maximum number of units to be installed
16 units (48 units when expansion units are connected)
Maximum number of I/O points
Maximum 3,096 points for expansion (KV-EB1S/KV-EB1R: When 2 units are expanded, 64-point I/O unit is used)
Bit device
Input relay R
Total 16,000 points 1 bit
Output relay R
Internal auxiliary relay R
Link relay B
16,384 points 1 bit
Internal auxiliary relay MR
16,000 points 1 bit
Latch relay LR
Control relay CR
640 points 1 bit
Word device
Timer T
4,000 points 32 bits
Counter C
Data memory DM
65,535 points 16 bits
Expansion data memory EM
File register
Memory bank switching mode FM
32,768 points × 4 memory banks 16 bits
Dial mode ZF
131,072 points 16 bits
Link register W
16,384 points 16 bits
Temporary data memory TM
512 points 16 bits
High-speed counter CTH
2 points 32 bits
4 points 32 bits (2 points for one high-speed counter)
Index register Z
12 points 32 bits
Control memory CM
6,000 points 16 bits
Positioning pulse output
2 points (maximum output frequency: 100 kHz)
CPU unit I/O
Input: 16 points, output: 8 points
Power failure hold function
Program memory
Flash ROM can be rewritten 100,000 times
Device
5 years (operating ambient temperature of 25°C in the power failure hold mode)*6
Self-diagnosis function
CPU abnormal, RAM abnormal, other
Internal current consumption
CPU unit: 320 mA or less
Expansion unit: KV-EB1S 15 mA or less, KV-EB1R 25 mA or less (except the drive current for input loop)
Weight
CPU unit: approx. 320 g
End unit: Approx. 30 g, Start unit for KV-5500/5000/3000: approx. 20 g
Expansion unit: KV-EB1S approx. 90 g, KV-EB1R approx. 115 g