AP3 AI3 4-20 mA loss warning in Schneider drive

1 Posts
1 Users
0 Reactions
162 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

An "AP3" AI3 4-20 mA loss warning on your Schneider drive indicates a loss of signal on Analog Input 3 (AI3). This means the drive isn't receiving a current within the expected 4-20mA range on that specific input terminal.

"AP3" "AI3 4-20 mA" loss warning on a Schneider drive indicates that the analog input AI3 is not receiving a valid 4-20 mA signal. This could be due to several reasons, such as a disconnected sensor, a broken wire, incorrect parameter settings, or issues with the signal source.

Steps to Troubleshoot and Resolve "AP3 AI3 4-20 mA Loss Warning":

  1. Verify Signal Source:

    • Check the device or sensor that is supposed to provide the 4-20 mA signal to AI3. Ensure it is powered and operational.
  2. Inspect Wiring:

    • Examine all wiring and connections between the sensor and the AI3 input on the drive. Look for loose, broken, or damaged wires. Ensure all connections are securely tightened and there is good contact at all terminals.
  3. Measure Current:

    • Use a multimeter to measure the current at the AI3 input. Verify that it falls within the 4-20 mA range. If the current is outside this range, it will trigger the warning.
    • Check for continuity in the current loop to ensure there are no breaks or interruptions.
  4. Check Parameter Settings:

    • Verify that the AI3 input is configured correctly in the drive parameters. Ensure that AI3 is set up to receive a 4-20 mA signal.
    • Review and adjust parameters related to AI3, such as input scaling, signal range, and any fault detection settings associated with AI3.
  5. Inspect Signal Conditioning (if applicable):

    • If there are signal conditioning devices (like isolators or converters) in the current loop, ensure they are functioning correctly and not causing the issue.
Share: